Dear all, I have a modbus TCP device which I am trying to read.
On the manufacturer’s guide I read the following (sorry if I translate to english not properly)
Data format corrensponds to the following standard types used in C programming language short consists of 2 bytes codified as 16 bit two's complement integer consists of 4 bytes codified as 4 bytes two's complement float consists of 4 bytes codified as IEEE 754 floating point on 32 bit double consists of 8 bytes codified as IEEE 754 floating point on 64 bit
All registers can be read using the Modbus function “03 : Read Holding Registers”
I am trying to read register number 0 (zero) which contains an integer of 4 bytes.
If I use the “modbus read data” tool within the data source editing page, I receive the following result:
0 ==> 0f55
1 ==> 2102
The result in the decimal sistem should be 35738895 (it is the serial number of the device, and I am sure of it because it is written on top of the device).
I’ve noticed that I could obtain the result if I compose the HEX number this way 0221550f, which means that I should put the above numbers in the following order:
4th couple 3rd couple 2nd couple 1st couple and convert it to decimal
Using the standard modbus data types which are available through the dropdown menu does not lead anywhere.
Do you gents have any idea on how I can resolve this issue?